/var/log/syslog has a large number of entries tracking these ARP replies, e.g.2021-06-04T18:46:02.359Z Manager1 NSX 6622 SWITCHING [nsx@6876 comp="nsx-edge" subcomp="datapathd" s2comp="arp" level="INFO"] ARP reply sent to 00:50:56:##:##:4a for 169.254.0.2 from 02:50:##:##:53:00 on lrouter port 0c456328-70e5-####-####-########3b1
2021-06-04T18:46:02.361Z Manager1 NSX 6622 SWITCHING [nsx@6876 comp="nsx-edge" subcomp="datapathd" s2comp="arp" level="INFO"] ARP reply sent to 00:50:56:##:##:4a for 169.254.0.2 from 02:50:##:##:53:00 on lrouter port 0c456328-70e5-####-####-########3b1
2021-06-04T18:46:02.361Z Manager1 NSX 6622 SWITCHING [nsx@6876 comp="nsx-edge" subcomp="datapathd" s2comp="arp" level="INFO"] message repeated 2 times: [ARP reply sent to 00:50:##:##:76:4a for 169.254.0.2 from 02:50:##:##:53:00 on lrouter port 0c456328-70e5-####-####-########3b1]
"Edge NIC Out of Receive Buffer" may be triggered on the Edge node.e.g.
> get dataplane cpu stats
Core : 2
Crypto : 0 pps
Intercore : 0 pps
Kni : 0 pps
Rx : 18460 pps <<
Slowpath : 0 pps
Tx : 18490 pps
Usage : 86% <<
VMware NSX-T Data Center
Incorrect logic in the DR of the ESXi hosts resulted in excessive ARP requests, for the SR/DR IP, being sent on the transit link to the Edge nodes.
This issue is resolved in VMware NSX-T Data Center 3.1.2 available at Broadcom Downloads.
If you are having difficulty finding and downloading software, please review the Download Broadcom products and software KB.
If you believe you have encountered this issue and are unable to upgrade, please open a support case with Broadcom Support and refer to this KB article.