Update failed at <TIME && DATE> - Elapsed Time : 22 minutes 24 seconds
Edge group upgrade status is FAILED for group <UUID> <UUID> :
[Prepare edge upgrade bundle https://<NSX_FQDN>/repository/4.2.3.3.0.25171318/Edge/nub/VMware-NSX-edge-4.2.3.3.0.25171324.nub
failed on edge TransportNode <UUID>: clientType EDGE, target edge fabric node id <UUID>, return status Download and verify bundle failed with msg:
Closing connection 5.].VMware NSX
SDDC 5.X
As a workaround, user should configure DNS on the edge appliances which are created using static management IP address and does not have a DNS configured on it. This is an issue in scale setups, where user has to go and configure DNS on each Edge Transport Nodes.
Steps:
configure_edge_dns.pyconfigure_edge_dns.py root@<manager-IP>:/tmp/ssh root@<manager-IP> python /tmp/configure_edge_dns.pyScript execution is going to be Interactive. If the FQDN requirement is disabled on the NSX Manager, it will print the following,
Output of the script when FQDN requirement is disabled on the NSX Manager:
FQDN requirement is not enabled on the NSX-T Manager. DNS configuration check is not required. Script executed successfully. |
If the FQDN requirement is enabled on the NSX Manager, and if there are edges created using static management address and do not have DNS configured on it, script will fetch the DNS configured on the NSX Manager and show that to the user, user can choose it or give a new DNS configuration. (Prefer the DNS configured on the NSX Manager) and the script will apply this DNS configuration on all the impacted Edge Transport Nodes.
Output of the script when FQDN requirement is enabled on the NSX Manager and the DNS is applied successfully on the required impacted Edge Transport Nodes:
FQDN requirement is enabled on the NSX-T Manager. DNS configuration is required on edge nodes which has static IP on the management interface. DNS Server IPs configured on NSX Manager: 10.#.#.# Do you want to use these DNS Server IPs set at NSX Manager? (yes/no): yes |
Logs on the script execution can be found at
Log location on the NSX Manager
/var/log/proton/configure_edge_dns_execution.log
Manual Workaround:
To check the DNS configuration on the Edge Node from the Admin CLI:
get config
If DNS and NTP are missing from the config, run the following commands:
set name-servers <DNS_IP_ADDRESS> set search-domains <####.com> set ntp-server <####.####.com>
Confirm the edge node now has the DNS and NTP configurations and then proceed with the upgrade
| From Version | To Version | Impact | NSX Manager Upgrade UI | Logs |
| Any version from 4.1.x and above | Any version to 9.0 or above | "DNS configuration check on the Edge" gets raised and blocks upgrade on UI | Log location on the NSX Manager: 2026-02-03T07:16:00.398Z WARNING pool-36-thread-8 UpgradeServiceImpl 2856583 SYSTEM [nsx@4413 comp="nsx-manager" level="WARNING" logger="UpgradeServiceImpl" msgID="SYSTEM" subcomp="upgrade-coordinator" threadName="pool-36-thread-8"] [PUC] Pre-upgrade check InspectionTaskInfo[acknowledgement=false,componentType=EDGE,description=This precheck prevents the upgrade from proceeding if DNS is not set up on an edge/VNA node that needs to download the upgrade nub via the NSX Manager URL using FQDN.,id=edgeDNSConfigCheck,name=DNS configuration check on the Edge/VNA,needsAcknowledgement=false,needsResolution=false,resolution=false,resolutionError=<null>] failed with result BasicInspectionTaskResult{status=FAILURE, taskInfo=InspectionTaskInfo[acknowledgement=false,componentType=EDGE,description=This precheck prevents the upgrade from proceeding if DNS is not set up on an edge/VNA node that needs to download the upgrade nub via the NSX Manager URL using FQDN.,id=edgeDNSConfigCheck,name=DNS configuration check on the Edge/VNA,needsAcknowledgement=false,needsResolution=false,resolution=false,resolutionError=<null>], failureMessages=null, failures=[{"moduleName":"upgrade-coordinator","errorCode":36011,"errorMessage":"DNS is not set up on Edge with ID 'ebaa####-e1a7-####-8564-a3b####0756d'. Cannot resolve the fqdn to fetch the upgrade bundle from NSX manager. Kindly refer to https://knowledge.broadcom.com/external/article/403857"}]}
| |
| Any version from 4.1.x and above | Any version to 4.1.x or 4.2.x | Edge upgrade will fail in download OS step, while downloading the NUB file. | Log location on the NSX manager: 2026-02-05T07:32:44.075Z INFO task-executor-7-1-workitem-EDGE-1####de-63d9-4##2-a##8-db#####e1##9 UcRepositoryServiceImpl 1405248 SYSTEM [nsx@6876 comp="nsx-manager" level="INFO" subcomp="upgrade-coordinator"] fqdn_required flag for (dc1###42-784c-4##b-c##d-c0b#####f874 : ipv4 192.1##.##0.0 ipv6 ##00::5:75) node is true.2026-02-05T07:33:16.704Z INFO task-executor-7-1-workitem-EDGE-EDGE-1####de-63d9-4##2-a##8-db#####e1##9-rpc UpgradeMessagingServiceImpl 1405248 SYSTEM [nsx@6876 comp="nsx-manager" level="INFO" subcomp="upgrade-coordinator"] decoding message, message bus type=com.vmware.nsx.upgrade_agent.PrepareUpgradeResponseMsg expected type=com.vmware.nsx.upgrade_agent.UagentMessage.PrepareUpgradeResponseMsg2026-02-05T07:33:16.704Z INFO task-executor-7-1-workitem-EDGE-EDGE-1####de-63d9-4##2-a##8-db#####e1##9-rpc UpgradeMessagingServiceImpl 1405248 SYSTEM [nsx@6876 comp="nsx-manager" level="INFO" subcomp="upgrade-coordinator"] decoded type=com.vmware.nsx.upgrade_agent.PrepareUpgradeResponseMsg msg=header { state: CMD_ERROR info: "* Trying (with httplib) sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net:443...\n* Closing connection 0\nWarning: Transient problem: Will retry in 1 seconds. 5 retries left.\n* Trying (with httplib) sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net:443...\n* Closing connection 1\nWarning: Transient problem: Will retry in 2 seconds. 4 retries left.\n* Trying (with httplib) sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net:443...\n* Closing connection 2\nWarning: Transient problem: Will retry in 4 seconds. 3 retries left.\n* Trying (with httplib) sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net:443...\n* Closing connection 3\nWarning: Transient problem: Will retry in 8 seconds. 2 retries left.\n* Trying (with httplib) sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net:443...\n* Closing connection 4\nWarning: Transient problem: Will retry in 16 seconds. 1 retries left.\n* Trying (with httplib) sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net:443...\n* Closing connection 5\ncurl_wrapper: (28) Failed to connect to sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net port 443: [Errno -3] Temporary failure in name resolution\n"2026-02-05T07:33:25.549Z INFO http-nio-127.0.0.1-7442-exec-4 UpgradeCoordinatorFacadeImpl 1405248 SYSTEM [nsx@6876 comp="nsx-manager" level="INFO" subcomp="upgrade-coordinator"] Component: EDGE, status: FAILED, % complete: 16.0, details: Prepare edge upgrade bundle https://sr026862-nsxmanager-ob-24278654-1-2602######49-###a-sr0####2.private.########.net/repository/4.2.3.0.0.24866349/Edge/nub/VMware-NSX-edge-4.2.3.0.0.24866356.nub failed on edge TransportNode EDGE-1####de-63d9-4##2-a##8-db#####e1##9: clientType EDGE , target edge fabric node id EDGE-1####de-63d9-4##2-a##8-db#####e1##9, return status Download and verify bundle failed with msg: Closing connection 5 ., canSkip: true |
Similar issue: NSX Edge upgrade stuck at 0% due to DNS resolution failure